Chad Mills
Member
I have a question regarding 408.41, which says "Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor." My question on this article is to do with the panels you see that are feed through. Alot of times there is only one neutral lug which is rated for 2 conductors. The manufacturers intent is for the installer to put the line in neutral and the line out neutral which is feeding a second section, both under the same lug. My question is whether this is up to code and if so why article 408.41 does not apply to this situation. I am assuming it has to be code or the big manufacturers would not be producing it this way. But it does't look up to code from what I read. Please advise.
Thank you
Chad
Thank you
Chad