rlrobinhood
- WY
- apprentice
Hi all,
I'm trying to understand the relationship between upgrading wire sizes to compensate for voltage drop and circuit protection. So, let me use an example:
A customer wants a 50 amp sub-panel 375' away from his main meter base. He will use this to power a 240 volt irrigation pump that requires 20 amp protection. Assuming an acceptable 5% voltage drop and 50 amp service at the subpanel, I believe the wire size should be #2 aluminum. The lugs on the sub-panel will accept this wire size. However, the 50-amp breaker (GE) at the main panel will not.
I believe there are two options to move forward on this:
1) Should the breaker on the main panel be up-sized to 100 amp to accept the upsized wire? I believe a 100 amp breaker is sized for #2 wire and the subpanel is rated at 100 amps.
2) Use a mechanical splice and splice the #2 aluminum wire to a short pigtail of #6 to allow for the connection to a 50-amp breaker.
I believe either of these is acceptable, what are your thoughts and preferences? Thanks in advance. I'm just struggling with the relationship between voltage drop and circuit protection. Many thanks!!