Question 10/15 Air over motor

Status
Not open for further replies.

maloo

Member
Location
Marion, Iowa
We do some agricultural work and have come across more 15 hp single phase motors. Recently a customer put in a axial fan that had a name plate rating of 10/15 Air over horsepower and 44/55 FLC.

I am assuming that the air over means you get a greater horsepower rating because of air passing over the motor cooling it similar to compressor motor being bathed in coolant. I am curious if I am correct on this?

Also do you size your overcurrent protection and wire off the name plate rating since there is no 15 hp column in 430.248?

Thanks for any help.

Baldor spec sheet
http://www.baldor.com/products/spec...s_FarmDuty&winding=37WGW198&rating=40CMB-CONT
 