I don't have the NEC handy to confirm an actual article citation. But I think his answer is correct, from just reading the question in context. I, for one, would not want a load that is actually classified as "emergency" to be included in the load shedding scheme.Enriquez said:My answer is (a) emergency based on article 517, but I'm not sure. I can't seem to find a definite either way. The only other thing I come up with is (d) none of these.........due to my lack of a definite answer.
Based upon 700.5 (b) in 05 I would say (a).
700.5 Capacity.
(B) Selective Load Pickup, Load Shedding, and Peak Load Shaving. The alternate power source shall be permitted to supply emergency, legally required standby, and optional standby system loads where the source has adequate capacity or where automatic selective load pickup and load shedding is provided as needed to ensure adequate power to (1) the emergency circuits, (2) the legally required standby circuits, and (3) the optional standby circuits, in that order of priority. The alternate power source shall be permitted to be used for peak load shaving, provided these conditions are met.
Peak load shaving operation shall be permitted for satisfying the test requirement of 700.4(B), provided all other conditions of 700.4 are met.
A portable or temporary alternate source shall be available whenever the emergency generator is out of service for major maintenance or repair.
The only place the code uses the word "branch" in association with loads is in Article 517 where we have the life safety, critical and equipment branch loads on the essential electrical system. The life safety and critical branches make up the emergency system. I would say that (a) is the correct answer.
The only place the code uses the word "branch" in association with loads is in Article 517 where we have the life safety, critical and equipment branch loads on the essential electrical system. The life safety and critical branches make up the emergency system. I would say that (a) is the correct answer.
The life safety and critical branches make up the "emergency system" for an Article 517 installation. That being said, I think that wirebender has it correct as the term "life safety" is the only one of the answers that has the word "branch" as the next word in the code book.Hmmm... to answer "a" would then seemingly permit shedding of "life safety". IMO, "life safety" should never be shed.
This is a confusing question. Taking another look at 517.30(B)(5) there is no provision that would permit the shedding of any of the loads listed in the question. The loads listed there are all required loads for an Article 517 installation.
Yes, I know that I have posted 3 different answers to this question....I believe this last one is correct.
517.26 Application of Other Articles. The essential electrical system shall meet the requirements of Article 700, except as amended by Article 517.
Roger,Don, the equipment branch can be shed, any particular equipment that must remain in operation can be supplied from the critical branch.
Roger
Roger,
Where does the NEC say that?
What is the equipment branch?
I cannot find it in the code.