question about 2 pole 120 arc fault breaker

Status
Not open for further replies.

kylelee

Member
Location
多伦多
If I run a 14/3 wire by using 2 pole arc fault breaker for 2 dedicated circuits as the pic
8d30743eabd8d8a0d8d30b276352b405.jpg
, but it looks this two circuits must on/off together. However, I don't want two different circuits on/off together. Can I just take out the common trip. And is it designed for 240v arc fault or 2 120 circuit?


从我的 iPhone 发送,使用 Tapatalk
 
Can I just take out the common trip. And is it designed for 240v arc fault or 2 120 circuit?

The "common trip" is done by the mechanism inside the body of the breaker and has nothing to do with the "handle tie."

The Code requirement for AFCI protection is only for 15 or 20 Amp 120 Volt. Now, a two-pole breaker is, ostensibly, a 240 / 120 Volt breaker, but I doubt the AFCI component is evaluated and listed for AFCI protection for 240 Volt loads.
 
The "common trip" is done by the mechanism inside the body of the breaker and has nothing to do with the "handle tie."

The Code requirement for AFCI protection is only for 15 or 20 Amp 120 Volt. Now, a two-pole breaker is, ostensibly, a 240 / 120 Volt breaker, but I doubt the AFCI component is evaluated and listed for AFCI protection for 240 Volt loads.

I believe so, and I read the instructions that it's designed for sharing neutral. Then the handle tie confusing me. Cause indeed I really don't need them on/off together


从我的 iPhone 发送,使用 Tapatalk
 
I believe so, and I read the instructions that it's designed for sharing neutral. Then the handle tie confusing me. Cause indeed I really don't need them on/off together


从我的 iPhone 发送,使用 Tapatalk
Do you have a multiwire branch circuit? If not use two single pole breakers. As mentioned "common trip" is internal, removing the handle tie will allow individual pole switching but when internals call for trip, both poles trip whether there is a handle tie or not.
 