so I’m dealing with a 3-phase, 4W, 120/208 volt panel with a main breaker that’s rated for 100A and has about 20,000 VAs loaded on it. That means, the total amperage should be about 55.6 amps. So on two different circuits (both different) I’m planning adding two heating elements, both of which consume about 250 watts each. So my idea was that each heater draws about 2.1 amps (they’re being supplied with 120VAC) for a total of 4.2 amps added to the circuit. So when I add the 500 to the panel load, it totals 20,500, and after doing the load calculation for it again, it totals to about 57 amps. Why? Wouldn’t it total to around 59.8 Amps based on what I calculated from the heaters?
The formula I’m using for calculating the load amps is I = Total power/(sqrt(3)*208).