question about an exam example question

Status
Not open for further replies.

bran82004

Member
Location
WISCONSIN, USA
This test question example was given and doesnt seem to be correct. the only way i can seem to make it work is by using the amp rating they give in the example. but when using the nec flc chart 430.250 the answer i came up with was 77.5A. which would require a #2 xhhw-2 conductor. any explanation would be great thanks..


3. A feeder supplies three 460-volt, three-phase, 1740 RPM, Design B, alternating-current
motors. The motors have the following nameplate ratings: 25 horsepower, 28.4 amperes; 15
horsepower, 18.2 amperes; and 10 horsepower, 11.3 amperes. Assuming all the motors are
operating under continuous duty, what minimum size XHHW-2 feeder circuit conductors are
required to supply the motor load? The conductor terminations are rated at 75?C.
Answer 4 AWG NEC 430.6, 430.24, 430.150, 310.16
 

cadpoint

Senior Member
Location
Durham, NC
I don't have a code Book to look at those Articles, I'm going to guess the "B" factor is involves or bad math of what your suppose do to the math with muliple motors...
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I also came up with the 77.5 amps.
With 75? termination, a #4 Cu rated at 85 amps would be sufficient.
Why did you select #2 ?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
This test question example was given and doesnt seem to be correct. the only way i can seem to make it work is by using the amp rating they give in the example. but when using the nec flc chart 430.250 the answer i came up with was 77.5A. which would require a #2 xhhw-2 conductor. any explanation would be great thanks..


3. A feeder supplies three 460-volt, three-phase, 1740 RPM, Design B, alternating-current
motors. The motors have the following nameplate ratings: 25 horsepower, 28.4 amperes; 15
horsepower, 18.2 amperes; and 10 horsepower, 11.3 amperes. Assuming all the motors are
operating under continuous duty, what minimum size XHHW-2 feeder circuit conductors are
required to supply the motor load? The conductor terminations are rated at 75?C.
Answer 4 AWG NEC 430.6, 430.24, 430.150, 310.16

You need to look at Table 430.250 to get the FLC of the motors listed in the example. Take your largest motor FLC x 1.25% then add the FLC of the other 2 motors. You then go to Table 310.16 under the 75 deg. column and find the ampacity for the total you came up with, then find your conductor size.
I also came up with 77.5A and #4AWG. You got the 77.5A correct, I don't see where you get #2AWG for that.
 
Last edited:

bran82004

Member
Location
WISCONSIN, USA
duh perfect example of reading the whole question

duh perfect example of reading the whole question

Right away when i was reading this question i saw the xhhw-2 and incorectly assumed they wanted the size based of an alum conductor. i now see that #4 xhhw-2 copper is suffecent for 85 amps. but thanks for the help
 

Finite10

Senior Member
Location
Great NW
You may very well se a question like that on a masters exam, but the largest motor is intermitent or short time duty cycle.

Then see 430.24, exc. 1. Pay attention to that word 'or' and then-
Check Table 430.22(E).
 