I'm installing 277 volt Metal-clad Cable (MC) with the use of connectors that do not use a locknut. The connectors have a screw that when tightened it compresses the metal-clad cable and secures it in the panel, box, etc. Would those type of connectors be listed for such a use.
250.97 bonding for over 250 Volts. For circuits of over 250 volts to ground, the electrical continuity of metal raceways and cables with metal sheaths that contain any conductor other than service conductors shall be ensured by one or more of the methods specified for services in 250.92 (B) except for (1)
Exception (d) Listed fittings that are identified for the purpose. I appreciate your input.
Justin W
250.97 bonding for over 250 Volts. For circuits of over 250 volts to ground, the electrical continuity of metal raceways and cables with metal sheaths that contain any conductor other than service conductors shall be ensured by one or more of the methods specified for services in 250.92 (B) except for (1)
Exception (d) Listed fittings that are identified for the purpose. I appreciate your input.