It states in 348.20 Size.
(A) Minimum FMC less than metric designator 16 (trade size 1/2) shall not be used unless permitted in 348.20(A)(1) through (5) for metric designator 12 (trade size 3/8)
(1) For enclosing the leads of motors as permitted in 430.145(B0
(2) In lengths not in excess of 1.8 m (6 ft)for any of the following uses:
a. For utilization equipment
b. As part of a listed assembly
c. For tap conductors to luminaries (lighting fixtures) as permited in 410.67(C)
(3) For manufactured wiring systems as permitted in 604.6(A)
(4) In hoist ways as permitted in 620.21(A)(1)
(5) As part of a listed assembly to connect wired luminaire (fixture) sections as permitted in 410.77(C)
Does it mean in (2c) "as part of a listed assembly" when you change from EMT to FMC using a change over fitting. I personally think that flex instead of EMT to FMC looks like crap. Though FMC does sometimes have its advantages for short runs. I have seen flex installed out of wire ways for thirty or forty feet instead of EMT changing to FMC. Is this legal. I am aware that over 6 ft a equipment grounding conductor must be installed. I personally don't trust any raceway as the equipment ground in itself. Thank you for your time in the misunderstanding of the wording used.
Justin
(A) Minimum FMC less than metric designator 16 (trade size 1/2) shall not be used unless permitted in 348.20(A)(1) through (5) for metric designator 12 (trade size 3/8)
(1) For enclosing the leads of motors as permitted in 430.145(B0
(2) In lengths not in excess of 1.8 m (6 ft)for any of the following uses:
a. For utilization equipment
b. As part of a listed assembly
c. For tap conductors to luminaries (lighting fixtures) as permited in 410.67(C)
(3) For manufactured wiring systems as permitted in 604.6(A)
(4) In hoist ways as permitted in 620.21(A)(1)
(5) As part of a listed assembly to connect wired luminaire (fixture) sections as permitted in 410.77(C)
Does it mean in (2c) "as part of a listed assembly" when you change from EMT to FMC using a change over fitting. I personally think that flex instead of EMT to FMC looks like crap. Though FMC does sometimes have its advantages for short runs. I have seen flex installed out of wire ways for thirty or forty feet instead of EMT changing to FMC. Is this legal. I am aware that over 6 ft a equipment grounding conductor must be installed. I personally don't trust any raceway as the equipment ground in itself. Thank you for your time in the misunderstanding of the wording used.
Justin