Breaker lockout devices are allowed on dishwashers and water heaters per code. I know of nothing to prevent them on a furnace. If there is someone please let me know. I have no problem in learning.
This has been discussed & cussed adinfitium. One method used here is a handy box with a single receptacle for the line side. For the load use a 3 ft pigtail. During a power outage you can plug the pigtail into an extension cord from a generator. This has satisfied the AHJ for means of disconnect.
This has been discussed & cussed adinfitium. One method used here is a handy box with a single receptacle for the line side. For the load use a 3 ft pigtail. During a power outage you can plug the pigtail into an extension cord from a generator. This has satisfied the AHJ for means of disconnect.
Might be a requirement in the mechanical code or some other code. Had a fire inspector ask for a disconnect on a boiler with a red cover even though the boiler was 5' away from the circuit breaker in the service.
I guess if AHJ wants to accept that, then so be it. There is such a thing as small transfer switches that would be NEC compliant.This has been discussed & cussed adinfitium. One method used here is a handy box with a single receptacle for the line side. For the load use a 3 ft pigtail. During a power outage you can plug the pigtail into an extension cord from a generator. This has satisfied the AHJ for means of disconnect.