GerryB
Senior Member
- Location
- woodbridge, ct. USA
A customer of mine has a 400 amp service, two 200 amp panels. He had a generator set up where they fed the two outside disconnects with no transfer or interlocks, relying on the HO to shut the mains to prevent backfeeding, so the solar company said to do it right. Since he had main breakers in his panels also I put interlock kits on each panel paralleled together to the generator. (this setup has been discussed on this forum, works perfectly, no way to backfeed to the disconnects outside. The generator power can only go as far as the back feed breaker in each panel, which can only be turned on when the main is turned off and the interlock moved accordingly.) Problem is since the solar company already saw it ( there was a bunch of professional looking notes and warnings on his outside disconnects about shutting the mains before turning on the generator), they asked the HO for the inspection release. Needless to say I didn't pull a permit and it was never mentioned as a need. Now I can still pull a permit. It's a small town and I have a good relationship with the inspector.My question is can't these solar guys see that it can't backfeed? What do they do normally when the do an install and the customer has some kind of generator set up? The owner is not getting a battery system which might be a problem.