Please help about method to determine grounding cable size from high mast and or lighting pole to the grounding rod?
Please help about method to determine grounding cable size from high mast and or lighting pole to the grounding rod?
Look at 410.30(B)Thanks all ,please introduce code references ?
Look at 410.30(B)
This article didnot show grounding cable size
I think we should refer to NFPA 780 about this regard as long the cable will be used to discharge the electrical strike,bonding the bolt to pole steel foundation could lead to galvanic corrosion, i am still searching for the article about that .
BTW, the bonding conductor size for Class 1 structures (75' or less) is 26,240 cir. mils or a #6 awg so if 780 does fit you are still OK with #6 awg
View attachment 14725
On our high mast luminaires we run a 2/0 to the ground ring from the pole and thre ring is also a 2/0
This is just to "eliminate static charges and dissipate the energy from a lightning event":thumbsup:
What about the high mast 30meter long and fitted by air terminal at the top to protect the lighting fixtures
Well if you put an air terminal up there it will need a full size down lead conductor at min 115,000 cir. mils but frankly it will not protect the light from damage in a strike rather may provide limited protection to surrounding structures. But once again this is optional IMO.
5.2.2 Electrically continuous metal structures shall require
only bonding to grounding electrode(s).