JJWalecka
Senior Member
- Location
- New England
I have a few question concerning the Grounding Electrode conductor.
Hypothetically, I have a 200 amp service. Table B.310.3 Ampacities of multi conductor cables with no more than three insulated conductors type USE, states that 2/0 AWG copper THHN @90 degrees Celsius is rated at 215 amperes. It is my understanding that there is no breakers or equipment rated for 90 degrees Celsius. 3/0 AWG copper at 75 degrees Celsius is rated at 213 amperes.
Table 250.66 Grounding Electrode Conductor for Alternating Current Systems states that copper 2/0-3/0 AWG the Grounding Electrode conductor is sized at 4 AWG.
250.64 Grounding Electrode Conductor installation
250.64(F)To Electrode(s)
A Grounding Electrode Conductor shall be permitted to be run to any convenient grounding electrode available in the grounding electrode system or to one or more grounding electrode(s) individually. The grounding electrode conductor shall be sized for the largest grounding electrode conductor required among all the electrodes connected to it.
250.53 Grounding Electrode System Installation
250.53(E) Supplemental Electrode bonding Connection Size.
Where the supplemental electrode is rod, pipe, or plate electrode, that portion of the bonding jumper that is the sole connection to the supplemental grounding electrode shall not be smaller than 6 AWG copper wire or 4 AWG aluminum wire.
If I'm interpreting this correctly the bond to the water meter street and load side would be 4 AWG copper, because the ground rod is the supplemental ground a 6 AWG is sufficient. If the water into the house was installed with pvc it couldn't be used as the main ground. The ground rods, pipe or plate electrodes would then be the primary ground? I would then have to use 4 AWG?
250.56 Resistance of rod, pipe, or plate electrodes.
A single electrode consisting of a rod, pipe, or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified by 250.52(A)(2) through (A)(7). Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall not be less than 1.8m (6ft) apart.
It was my understanding that if 25 ohms or less was not apparent then you had to install more electrodes till 25 ohms or less was reached. Unless I'm reading this wrong, if 25 ohms or less is not reached than one additional electrode, specified in 250.52(A)(2) through (A)(7), would be installed?
Please enlighten me upon my misunderstanding. Thank you for your time and effort.
Justin
Hypothetically, I have a 200 amp service. Table B.310.3 Ampacities of multi conductor cables with no more than three insulated conductors type USE, states that 2/0 AWG copper THHN @90 degrees Celsius is rated at 215 amperes. It is my understanding that there is no breakers or equipment rated for 90 degrees Celsius. 3/0 AWG copper at 75 degrees Celsius is rated at 213 amperes.
Table 250.66 Grounding Electrode Conductor for Alternating Current Systems states that copper 2/0-3/0 AWG the Grounding Electrode conductor is sized at 4 AWG.
250.64 Grounding Electrode Conductor installation
250.64(F)To Electrode(s)
A Grounding Electrode Conductor shall be permitted to be run to any convenient grounding electrode available in the grounding electrode system or to one or more grounding electrode(s) individually. The grounding electrode conductor shall be sized for the largest grounding electrode conductor required among all the electrodes connected to it.
250.53 Grounding Electrode System Installation
250.53(E) Supplemental Electrode bonding Connection Size.
Where the supplemental electrode is rod, pipe, or plate electrode, that portion of the bonding jumper that is the sole connection to the supplemental grounding electrode shall not be smaller than 6 AWG copper wire or 4 AWG aluminum wire.
If I'm interpreting this correctly the bond to the water meter street and load side would be 4 AWG copper, because the ground rod is the supplemental ground a 6 AWG is sufficient. If the water into the house was installed with pvc it couldn't be used as the main ground. The ground rods, pipe or plate electrodes would then be the primary ground? I would then have to use 4 AWG?
250.56 Resistance of rod, pipe, or plate electrodes.
A single electrode consisting of a rod, pipe, or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified by 250.52(A)(2) through (A)(7). Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall not be less than 1.8m (6ft) apart.
It was my understanding that if 25 ohms or less was not apparent then you had to install more electrodes till 25 ohms or less was reached. Unless I'm reading this wrong, if 25 ohms or less is not reached than one additional electrode, specified in 250.52(A)(2) through (A)(7), would be installed?
Please enlighten me upon my misunderstanding. Thank you for your time and effort.
Justin