I have Griddle that is 9 kVA at 208V three phase. The engineer has provided 40A breaker and 50A receptacle.
FLA is 24.98A with 1.25% should give 31.22A.
Question should not the breaker be 35A instead of 40A?
FLA is 24.98A with 1.25% should give 31.22A.
Question should not the breaker be 35A instead of 40A?