A vendor is selling us a system sending 48 VDC ranging from 5A to 10 A from a DC converter in an Equipment Rack up seven floors in a cable shaft to power Communications Processors.
The Amps would vary with the number of Communication Processors. This would be a Class 3 application since its greater than 100VA. The vendor is using 10 AWG 2 conductor stranded cable.
The cable shaft contains Communications cabling as well as 120 VAC AC circuits in conduit.
The vendor is using Plenum Cable.
We’re trying to verify the vendor’s cable selection
Article 725 says CL3R applies.
We can’t locate 10 AWG-2 CL3R cable anywhere. We can find it in smaller gauges, around 12 to 18 AWG.
What make us feel queasy is the insulation is usually a thin PVC jacket and is minimal.
Also its always called "remote control and alarm cable"
48 VDC at 10 A seems substantial.
Is there anyway we can require the vendor to use 10 AWG/2 MC cable in this application?
The Amps would vary with the number of Communication Processors. This would be a Class 3 application since its greater than 100VA. The vendor is using 10 AWG 2 conductor stranded cable.
The cable shaft contains Communications cabling as well as 120 VAC AC circuits in conduit.
The vendor is using Plenum Cable.
We’re trying to verify the vendor’s cable selection
Article 725 says CL3R applies.
We can’t locate 10 AWG-2 CL3R cable anywhere. We can find it in smaller gauges, around 12 to 18 AWG.
What make us feel queasy is the insulation is usually a thin PVC jacket and is minimal.
Also its always called "remote control and alarm cable"
48 VDC at 10 A seems substantial.
Is there anyway we can require the vendor to use 10 AWG/2 MC cable in this application?