9-11 Log #3091 NEC-P09 Final Action: Reject
(312.5)
____________________________________________________________
Submitter: Joseph A. Hertel, Safety and Buildings
Recommendation: Revise as follows:
Cabinets, cutout boxes, and meter socket enclosures [NEC 312.5]. (1) Cables
[NEC 312.5(C)] Substitute the following wording for 312.5(C) Exception
(intro):
Exception: Cables with entirely nonmetallic sheaths shall be permitted to
enter an enclosure through one or more nonflexible raceways of not less than a
fitting and not more than 10 ft in length, provided all of the following
conditions are met:
Delete 312.5(C) Exception paragraph (b).
Substitute the following wording for 312.5(C) Exception paragraph (c):
A fitting is provided on each end of the raceway to protect the cable(s) from
abrasion.
Substantiation: The required 18 in. length prevents use of this wiring method
in many instances. Reducing the length to that of a fitting would not create a
hazard. This method is becoming quite common where panels are placed in an
exterior location.
(b) A fitting or raceway used in this manner would have the same
characteristics if it was attached to the sides or bottom of the enclosure.
(c) The current language requires that the fittings remain accessible after
installation. This method is used in multifamily dwellings to bring the branch
circuits into a cabinet and the end of the raceway is not accessible after the
gypsum wall covering is installed. There is no real need for the accessibility
since modifications to the branch circuitry of multifamily dwellings are rarely
encountered.
Panel Meeting Action: Reject
Panel Statement: With respect to the three modifications proposed by the
submitter, the panel provides the following response:
1) The 18 inch minimum raceway length was chosen as a distance long
enough to provide reasonable containment of the enclosed cables without
specifying a length so long as to require mandatory derating of the cables.
Removal of this length requirement would create the possibility that the
enclosure will no longer perform its intended containment function (A95 ROP
? 9-66a).
2) The exception was written to allow such installations only at the top of the
enclosure as the panel noted this limitation would assure that the outer raceway
termination wouldn?t be readily accessible (A98 ROC ? 9-44).
3) The current language not only requires the fitting to remain accessible, but
also requires that the enclosure be surface-mounted.
Adequate closure of the enclosure is dependent upon adequate closure of the
raceway. No fittings are designed and evaluated to close openings around
multiple cables as anticipated by the proposal. The lack of suitable fittings
presents the possibility that excess dust, debris, rodents or other pests could.......