I am installing an explosion proof emergency stop pushbutton box inside of a spray paint booth. The pushbutton box is located on the inside wall of the booth. There will be two 90 degree xp fittings leaving the bottom of the xp box with a conduit seal on the second 90 degree fitting going up the outside wall of the booth with 1/2" RMC. The sealing fitting is required in 501.15(a)(1). According to 501.15(a)(4), a sealing fitting is required as the conduit leaves ' the C1D1 boundary, and must be located within 10' of the boundary, on either side of the boundary. The first sealing fitting is located within 6' of the C1D1 boundary, with 6' being within the 10' requirement. Will this first sealing fitting suffice, or do I have to install a second sealing fitting at the C1D1 boundary ? Thank You, Steve Wiese.