any body can help about suitable direct buried cables types to be run in green landscape areas where we have trees, palms , complete irrigation system?code references please
What are the cables powering?
Landscape lighting
both of the two casesLow voltage? Line voltage?
both of the two cases
Take a look at table 300.5 and consider how deep you must bury different items in different circumstances and make a decision on what works best for you.
For line voltage you could be a little as 6 inches deep but must be in RMC. Otherwise for a direct buried cable it jumps to 24 inches deep. Other conditions mentioned in the table can vary these figures.
Yes but how deep you must bury them depends on if they are high or low voltage and a few other conditions in the table I mentioned.if i want to use a direct buried cables is it possible to use UF or armored cables in landscape areas to feed landscape lighting where there is irrigation system is working there?