These days, no common neutral?...
That was my first thought, too. It's been a LONG time since I used plans on new construction, but I think the symbols mean three hots, three "neutrals," and a ground? Makes me wonder what the benefit is unless this is in conduit (term includes EMT...) and they are saving pipe.
Are ckts 10 and 14 nearby? It looks like a 3-ckt homerun to me, and then the other two will go from there to ....
Thanks, that's kind of what I thought (and am used to) but one of the circuits is a good distance away in another room so it didn't seem correct. I guess it's possible the architect and I have a different idea of how the circuits should be run.
sometimes the way the engineer denotes a homerun on your power prints makes more sense when you check how the circuit is identified on the panel schedule.. which is a great way to find out it may be a mistake, or correct. or, even realize it may be the wrong panel. i have learned the panel schedule is, in the end, the absolute of what you are selling the customer, regardless of discrepancys on the power prints. however, the number and location of actual power outlets are absolute... err- usually! always dble check all your sheets, especially when it comes to your equipment schedules on the hvac schedules.
With the common disconnect requirement for MWBCs in 210.4(B), it has been a long time since I have seen an engineered set of drawings that permitted multi-wire branch circuits.I saw three neutrals! I thought we were trying to save the planet. Now, more wire is being used, not less!
With the common disconnect requirement for MWBCs in 210.4(B), it has been a long time since I have seen an engineered set of drawings that permitted multi-wire branch circuits.