If the OCPD is ahead of the circuit I use table 250.122 for the EGC. ????
I have a plug in bus bar non-fused disconnect that feeds a 75 amp disconnect breaker for a CNC machine, So.
will the OCPD be behind.??? Do I used table 250.102 for the EGC???
There is no fuse in the bus plug disconnect, and the next OCPD is the 75 amp disconnect breaker for the CNC machine. Or do I use 250.102, for the
sizing of the EGC.
Thank you all, for any and all information.