I was doing a job the other day and had some questions about a transformer and its correlation. I will try and explain the situation and would like as much help in understanding what was happening.
What I saw when i got on the job was a 3 phase 240 (what i thought to be a delta since there was no neutral, however there was also no stinger leg initially.) There was 120v to ground on all 3 phases. Between "A" phase and "B" phase was 240v, between "A" phase and "C" Phase was 240v, however between "B" Phase and "C" was no voltage.
There was a 240v to 120v Transformer being fed by a 20amp 2Pole Breaker on the "B" and "C" phases that fed a few 120v receptacles and lights. Because it was on the "B" and "C" phases which was not getting 240v between each other the transformer was not working properly. So I moved the transformer onto the "A" and "B" phases and the transformer now correctly worked.
This is where i got confused. After I moved the breaker feeding the transformer onto the "A" and "B" phases I was reading the following voltages to ground: "A" phase 120v, "B" phase 120v, "C" 206v. between any of the 3 phases i was reading 240v.
Sorry for the long post, but I would like to be thorough with what I do and need a better understanding of what is going on so any help is much appreciated.
What I saw when i got on the job was a 3 phase 240 (what i thought to be a delta since there was no neutral, however there was also no stinger leg initially.) There was 120v to ground on all 3 phases. Between "A" phase and "B" phase was 240v, between "A" phase and "C" Phase was 240v, however between "B" Phase and "C" was no voltage.
There was a 240v to 120v Transformer being fed by a 20amp 2Pole Breaker on the "B" and "C" phases that fed a few 120v receptacles and lights. Because it was on the "B" and "C" phases which was not getting 240v between each other the transformer was not working properly. So I moved the transformer onto the "A" and "B" phases and the transformer now correctly worked.
This is where i got confused. After I moved the breaker feeding the transformer onto the "A" and "B" phases I was reading the following voltages to ground: "A" phase 120v, "B" phase 120v, "C" 206v. between any of the 3 phases i was reading 240v.
Sorry for the long post, but I would like to be thorough with what I do and need a better understanding of what is going on so any help is much appreciated.