Greetings, I have been a licensed electrician for quite a long time (79 to be exact). My understanding of common trip breakers are to protect 220 volt circuits. I had an inspector this week turn down a new service because I did not use common trip breakers for two circuits sharing the same neutral. I fed back to the original panel for 12 circuits with 6 neutrals, and balanced the load on the new breakers accordingly, no ACFI or GFCI circuits in the mix. He said that either every circuit HAD to have their own neutral, or I had to put common trip breakers in place for these two circuits.
Is this a new code, or a misunderstanding by the inspector? I obviously can buy the Quad double common trip set up breakers to get around this infraction... beings adding 6 more neutrals will almost be impossible in the existing conduit, but I would rather know if he is making something up; or I have missed a code that I should have known. Granted, being in the business for some 35+ years, I have seen a lot of code changes... some I have been on top of; some slip by. I am not an argumentive person and would never argue with an inspector unless I felt I was right and never wanted to work in that city again! I have a problem with a common trip on what used to be an acceptable 3 wire dual circuit.
Thank you. Randy W
Is this a new code, or a misunderstanding by the inspector? I obviously can buy the Quad double common trip set up breakers to get around this infraction... beings adding 6 more neutrals will almost be impossible in the existing conduit, but I would rather know if he is making something up; or I have missed a code that I should have known. Granted, being in the business for some 35+ years, I have seen a lot of code changes... some I have been on top of; some slip by. I am not an argumentive person and would never argue with an inspector unless I felt I was right and never wanted to work in that city again! I have a problem with a common trip on what used to be an acceptable 3 wire dual circuit.
Thank you. Randy W