90.4( C) Explanatory Material. Explanatory material, such as references to other standards, references to related sections of this Code, or information related to a Code rule, is included in this Code in the form of informational notes. Such notes are informational only and are not enforceable as requirements of this Code. ...
Or if you live in NYC there is a city amendment 210.19(A)(1) that makes it mandatory to keep VD to 3% and 5%
nyc amendment
It is not as important as many make it out to be. Most any electrical equipment can operate just fine with as much a 10% below nominal voltage ratings.Thank you guys for these so helpful explanations ,but still wanna ask as u know V.D is important in design and affected important loads such as lighting ,motors ,why is it just informational note not a mandatory section -values -in Nec
I guess you have to assume the max-- 15 or 20 amps depending on the circuit. IDKHow do you know the load on a general purpose branch circuit?
It is not as important as many make it out to be. Most any electrical equipment can operate just fine with as much a 10% below nominal voltage ratings. When specific loads and specific voltage levels are required good design an professional installers would be in order. The NEC is a guideline for safe electrical installations, not a design manual.
How do you know the load on a general purpose branch circuit?
I guess you have to assume the max-- 15 or 20 amps depending on the circuit. IDK