eric9822
Senior Member
- Location
- Camarillo, CA
- Occupation
- Electrical and Instrumentation Tech
I work in a large industrial facility and one of my responsibilities is to ensure that all installations comply with the NEC. We have a project going on now that includes the installation of a several servo drives and motors. The manufacturer has supplied 75 foot pre-terminated cables for each drive and motor, all of the cables are marked AWM. My position is that these cables cannot be field installed in raceway, cable tray, wireway, etc. The manufacturer and my corporate hierarchy states that the cables are OK because the motors, drives, and cables are UL listed as an assembly AND fall under NFPA79. My rebuttal to that was "If that is true then I should be able to install any UL listed equipment in any manner I choose"; I don't think that is correct. What do you say?