question for sizing a circuit for a in-ground pool heater circuit
MMEelectric
bensalem PA
Hello I was asked to install the circuit needed for a pool heater. Here is what's on the side of the heater. The run is approx 170' and will be in PVC conduit buried under ground. I want to know what size breaker and copper wire to use. Do I also need to drive a ground rod? This is my first time doing one of these and want to make sure I don't miss anything. Thank you
POOL HEAT PUMP
NOTE: OUTDOOR USE / UTILISATION À L'EXTÉRIEUR
MODEL NUMBER SHAS-137H-UU
RATED VOLTAGE / FREQUENCY 208-230VAC~ 1 PH/60HZ
RATED HEATING CAPACITY 137000Btu/h
TOTAL LOAD / MAX FUSE 30.1A / 70A
FAN MOTOR FLA 2.1 HP 0.41
COMPRESSOR RLA 41.4 LRA 196
MINIMUM CIRCUIT AMPACITY 54A
infinity
New Jersey
Journeyman Electrician
You can use #6 THWN copper with a 70 amp OCPD. Ground rods are not required unless you're installing a feeder and a sub-panel for the pool.
LarryFine
Henrico County, VA
Electrical Contractor
Welcome to the forum.
Here's what matters:
MAX FUSE 70A
Just like HVAC equipment, size the wire for 54a (or more), and fuses (not a breaker) of 70a (or less).
As infinity said, a single circuit doesn't need an electrode, but if it's a feeder, the sub-panel would.
Little Bill
Tennessee NEC:2017
Semi-Retired Electrician
Even if so, there would be a much smaller current difference, and the lower voltage would have the higher current.
I noticed that too but didn't check it. I'm recouping from surgery and don't see things clearly. I need to shut the keyboard off and just read!:(