Question for you "old" guys...

Status
Not open for further replies.

NolaTigaBait

Senior Member
Location
New Orleans,LA
ive noticed on several houses that ive done service calls to that aluminum feeders were used to feed a subpanel...the last one that i went to they used a #4 aluminum w ground feeder to feed a subpanel, it ws protected by a 100 amp breaker...the breakers look original and obviously so is the wire...my question is, back in the 60's and 70's, was aluminum wiring considered equivelent to copper?....b/c if not, i can't see how this passed initial inspection
 

ohm

Senior Member
Location
Birmingham, AL
ive noticed on several houses that ive done service calls to that aluminum feeders were used to feed a subpanel...the last one that i went to they used a #4 aluminum w ground feeder to feed a subpanel, it ws protected by a 100 amp breaker...the breakers look original and obviously so is the wire...my question is, back in the 60's and 70's, was aluminum wiring considered equivelent to copper?....b/c if not, i can't see how this passed initial inspection

I'm not real old but even my first code book (58) didn't allow that.
 

480sparky

Senior Member
Location
Iowegia
I'm not real old but even my first code book (58) didn't allow that.

'56 is the first year aluminum conductors were specifically 'tabled' (Table 1a, Chapter 10) for ampacity. Prior to that, the rule was aluminum had 84% of the capacity of a copper conductor of the same size.
 

ohm

Senior Member
Location
Birmingham, AL
'56 is the first year aluminum conductors were specifically 'tabled' (Table 1a, Chapter 10) for ampacity. Prior to that, the rule was aluminum had 84% of the capacity of a copper conductor of the same size.


Well 480 you get he prize for travelling the furthest to this reunion!
 

tryinghard

Senior Member
Location
California
...my question is, back in the 60's and 70's, was aluminum wiring considered equivelent to copper?....b/c if not, i can't see how this passed initial inspection

Here in the ?otts? aluminum used correctly is just fine compared to copper. It?s usually a price issue but sometimes a preference.
 

Mule

Senior Member
Location
Oklahoma
my question is, back in the 60's and 70's, was aluminum wiring considered equivelent to copper?....b/c if not, i can't see how this passed initial inspection

In our town in the 60's and 70's, alot of things were passed if you offered a 1/5 of whiskey for a permit fee....:D
 

480sparky

Senior Member
Location
Iowegia
In our town in the 60's and 70's, alot of things were passed if you offered a 1/5 of whiskey for a permit fee....:D

Then again, how much work that was done back in the 60s and 70s were even required to be inspected? Maybe back then, they just trusted the workers to do it right and had no permit/license/inspection program in place.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
ive noticed on several houses that ive done service calls to that aluminum feeders were used to feed a subpanel...the last one that i went to they used a #4 aluminum w ground feeder to feed a subpanel, it ws protected by a 100 amp breaker...the breakers look original and obviously so is the wire...my question is, back in the 60's and 70's, was aluminum wiring considered equivelent to copper?....b/c if not, i can't see how this passed initial inspection


Many things passed inspection that shouldn't have. When I first moved to NC the county adjacent to us didin't even have an inspection department. EC did what they wanted. Some inspectors where I lived wouldn't even come up the driveway to inspect the house- they would sign off at the box at the bottom of the drive. Sad but true.
 

iwire

Moderator
Staff member
Location
Massachusetts
ive noticed on several houses that ive done service calls to that aluminum feeders were used to feed a subpanel...the last one that i went to they used a #4 aluminum w ground feeder to feed a subpanel, it ws protected by a 100 amp breaker...the breakers look original and obviously so is the wire...my question is, back in the 60's and 70's, was aluminum wiring considered equivelent to copper?....b/c if not, i can't see how this passed initial inspection


Are you sure it is AL and not tin plated copper?
 

SEO

Senior Member
Location
Michigan
Are you sure it is AL and not tin plated copper?

I agree with Bob just by looking at the conductor the tin plated copper conductors are hard to tell apart from al. It's sad to say but some inspectors are lazy and do not do a thorough job. It's a lot easier to pass a job than to write a violation. But they have to live with themselves and the consequences.
 