I'm looking to install a new sub panel for multiple EV charging stations and I'd like to maximize the amount of stations the customer can install. The chargers require (2) 40a 208v single phase circuits which makes staying under 80% capacity and balancing the load for maximum capacity a bit difficult.
Ideally, if we can get away with running the panel at 100% I'd like to do it.
Please let me know if I'm understanding the exception below, specifically the underlined portion. The way I'm reading it, if we install a 400 amp panelboard rated for 100% load with main breaker rated at 100%,i still need all of my branch circuit OCPD's to also be rated at 100% even if they are only loaded to <80%? I want to load the panel feeders and main breaker at 100%, not the individual branch circuits, but it looks like a catch-22 based upon my understanding of the code section below. I haven't asked my supplier if 40A breakers rated for 100% use are available, but after a brief googling it doesn't look like they are.
"
As explained in Section 210-20(a) of the 1999 National Electrical Code
(NEC):
�Where a branch circuit supplies continuous loads or any combination of
continuous and noncontinuous loads, the rating of the overcurrent device
shall not be less than the noncontinuous load plus 125 percent of the
continuous load.
�Exception: Where the assembly, including the overcurrent devices
protecting the branch circuit(s), is listed for operation at 100 percent of its
rating, the ampere rating of the overcurrent device shall be permitted to be
not less than the sum of the continuous load plus the noncontinuous load.�
Ideally, if we can get away with running the panel at 100% I'd like to do it.
Please let me know if I'm understanding the exception below, specifically the underlined portion. The way I'm reading it, if we install a 400 amp panelboard rated for 100% load with main breaker rated at 100%,i still need all of my branch circuit OCPD's to also be rated at 100% even if they are only loaded to <80%? I want to load the panel feeders and main breaker at 100%, not the individual branch circuits, but it looks like a catch-22 based upon my understanding of the code section below. I haven't asked my supplier if 40A breakers rated for 100% use are available, but after a brief googling it doesn't look like they are.
"
As explained in Section 210-20(a) of the 1999 National Electrical Code
(NEC):
�Where a branch circuit supplies continuous loads or any combination of
continuous and noncontinuous loads, the rating of the overcurrent device
shall not be less than the noncontinuous load plus 125 percent of the
continuous load.
�Exception: Where the assembly, including the overcurrent devices
protecting the branch circuit(s), is listed for operation at 100 percent of its
rating, the ampere rating of the overcurrent device shall be permitted to be
not less than the sum of the continuous load plus the noncontinuous load.�