I believe this section means if you run larger conductors for voltage drop, like # 10's for a 20 amp circuit, then your ground wire would also have to be #10 because it is the same circular mill as the ungrounded conductors. (the wording about being increased in size "proportionately" is what confuses me, since the egc is often smaller.) Do I have this right?
In relation to this, a question came up about grounding/bonding the gas "tract" pipe. Around here a #6 is run from the corrugated gas pipe knuckle to the ground rods, water meter, or into the panel. (The plumber is allowed to do either of the first two methods.) But in this case it is new construction with temporary heat and a temp service about a hundred feet away. The question was could a ground rod be driven at the building and be done with it.
The answer from a state BO was "no, it has to go to the rods at the temp service." He also added that you should have an electrician do it because of the distance involved, which got me considering 250.122(B). Since there are no conductors here I am thinking there is no reason to increase the size of this ground wire. Any thoughts?
In relation to this, a question came up about grounding/bonding the gas "tract" pipe. Around here a #6 is run from the corrugated gas pipe knuckle to the ground rods, water meter, or into the panel. (The plumber is allowed to do either of the first two methods.) But in this case it is new construction with temporary heat and a temp service about a hundred feet away. The question was could a ground rod be driven at the building and be done with it.
The answer from a state BO was "no, it has to go to the rods at the temp service." He also added that you should have an electrician do it because of the distance involved, which got me considering 250.122(B). Since there are no conductors here I am thinking there is no reason to increase the size of this ground wire. Any thoughts?