Could someone look over this three phase load calculation?
This is a subpanel load calculation for an existing multifamily building with 2000A service and several subpanels.
The house panel has a 600A 208Y/120 3 phase 4 wire feed. The original plan set reads:

My question is the EVCS calculation. The 7700 VA is counted at 125%. Then the overall load is raised by 125%.
Is the load calculation correctly done? Is the EVSE continuous load portion double counted?
-
And what rule allowed a 600A breaker on a 605A calculated load?
The actual EV loads are listed in the same document as 22 KAIC, with all loads as "Lighting":


This is a subpanel load calculation for an existing multifamily building with 2000A service and several subpanels.
The house panel has a 600A 208Y/120 3 phase 4 wire feed. The original plan set reads:

My question is the EVCS calculation. The 7700 VA is counted at 125%. Then the overall load is raised by 125%.
Is the load calculation correctly done? Is the EVSE continuous load portion double counted?
-
And what rule allowed a 600A breaker on a 605A calculated load?
The actual EV loads are listed in the same document as 22 KAIC, with all loads as "Lighting":