Pythagorean's theorem.Thanks Don.
How this formula is derived?
Well if you are actually utilizing the center tap of said winding you now have a three phase 4 wire delta system. Pole pig transformer banks often have center tap on every pig in a delta configuration, but they either corner ground one corner or ground only one midpoint and leave the others floating.Why would there be a center tap on one winding in a 3 wire delta system?
And where are you seeing a 370V delta system in the first place?
Thank you sir!Pythagorean's theorem.
Side C = Line-Line voltage (Vll)
Side A = Line-center tap voltage (1/2 x Vll)
Solve for Side B
.866 is SQRT3 divided by 2, so yes.Can't you also multiply 370v ph-ph x .866, to find the same.fir a center tapped delta. That is how I was taught. The .866 is the teaser tap on a scott T xfrmr true 2 phase 4 w setup, and also inversely the relation of a high leg to ground verus the phase to phase on a center tapped delta system, or a 4w delta.( why the smoke comes out when you use the bastard leg, for outlets) Which is always half voltage p-N or G if it's truly 4 wire delta on the other two legs. On tthe third is your bastard leg. Had lots of both the first place I worked. One system there supplying 120v outlets from a 4w delta and small motors at 240v 3 phase, one supplying 2 phase 4 wire motors from the turn of last century. The old guy that held my hand there learning the systems Also taught me in the few places we had 2 phase, 3 wire that the proverbial B phase carried the sum of currents and was larger by 1.414x, which also is the multiplier for 45* offsets. He was 76 I was 18. I wish he was still live. Would love to pick that brain.
In 19 years doing this, that was never explained so easily. Everyone should know 120/208/240 from a 4w Delta. Never put the 208/120 part together. Never had it explained so succinctly. The oddball systems we had, was a simple way for me to remember. Thank you! Working aboard ships now, and everything is a delta, and ungrounded, even the 120v outlet for a phone charger. A Wye system is incredibly foreign. Now. Even the 4160 stuff is an ungrounded delta, a real oddball. 2 things I do remember. Don't get in series with a 277v neutral, and 277 is miserable to get whacked from.866 is SQRT3 divided by 2, so yes.
Formula is basically half line to line volts times SQRT 3 - if you draw the delta out that is what you would be measuring, mid way point of one side to the opposite corner.
...And where are you seeing a 370V delta system in the first place?