trojans4
Member
- Location
- Iowa
- Occupation
- Semi -retired master electrician. Fully retired math and physics teacher.
408.40 states in part "Equipment grounding conductors shall not be connected to a terminal bar provided for grounded conductors unless the bar is identified for the purpose and is located where interconnection between equipment grounding conductors and grounded conductors and grounded circuit conductors is permitted or required by Article 250". On a residential/commercial 200A main service panel my understanding is that the neutrals and grounds should land on separate terminal bars even though both terminal bars are bonded to the panel with the reason being there are different termination requirements for grounds and neutrals as pointed out in this article and Article 408.41. My question is about the bold portion. How would a bar be identified for this purpose? What kind of bar would allow both grounds and neutrals to be terminated on it? In a discussion with other electricians I know, resulting from a post on another site, I have been told all terminal bars are listed for either neutrals or grounds so you do not have to have two separate terminal bars in the main panel. I think they are mistaken and am wondering what experts on this forum have to say.