jango Senior Member Mar 4, 2010 #1 Distance: 325 ft. feeding a 200A rated sub panel with a total connected load of approx. 150 amps max. Can someone recommend the minimum THHN copper wire size and PVC schedule 40 conduit size?
Distance: 325 ft. feeding a 200A rated sub panel with a total connected load of approx. 150 amps max. Can someone recommend the minimum THHN copper wire size and PVC schedule 40 conduit size?
NolaTigaBait Senior Member Location New Orleans,LA Mar 4, 2010 #2 Sure...do a voltage drop calulation, then use table 310.15..boom , done.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Mar 4, 2010 #3 You can try this one for the VD: http://www.elec-toolbox.com/calculators/voltdrop.htm Look up the conduit fill in Chapter 9.
You can try this one for the VD: http://www.elec-toolbox.com/calculators/voltdrop.htm Look up the conduit fill in Chapter 9.
raider1 Senior Member Staff member Location Logan, Utah Mar 4, 2010 #4 What is your voltage and is this single phase or 3 phase? Chris
W wbw1989 Member Mar 4, 2010 #5 For "MINIMUM" 3/0-3/0-3/0-6awg in a 2 inch conduit. However, that is the minimum not accounting for an easy pull and voltage drop.
For "MINIMUM" 3/0-3/0-3/0-6awg in a 2 inch conduit. However, that is the minimum not accounting for an easy pull and voltage drop.