Question on a 200 amp feeder???

Status
Not open for further replies.

jango

Senior Member
Distance: 325 ft. feeding a 200A rated sub panel with a total connected load of approx. 150 amps max.

Can someone recommend the minimum THHN copper wire size and PVC schedule 40 conduit size?
 

wbw1989

Member
For "MINIMUM" 3/0-3/0-3/0-6awg in a 2 inch conduit. However, that is the minimum not accounting for an easy pull and voltage drop.
 