The existing building has a piece of switchgear fed thru a outside junction box then goes to the Poco transformer.There is now a addition and I am wanting to add another panel beside the existing and feed from same junction box, does this still qualify as one service. The transformer and secondary wires can carry the new load. The existing bond to the building steel is based on parallel #3/0cu , the new panel will have parallel #750al. do I leave existing bond intact and add another for new panel. The Gec system is 2 ground rods only and I don't believe I can access the rods(poured over with concrete ) so would you drive 2 new rods and loop both panels thru these. I am sorry for all the questions just dealing with old existing and trying to wrap my head around this. I am fine on the 6 disconnect rule.