Question on ampacity

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have SE 14.4k inverter 208V three phase output. On the DC inverter side I have EMT condit with 6 #10 Thwn-2 + #8 Gnd from inverter which is inside the building to outside to roof. On the roof under solar panels I have junction box which transtion cable to 6 #10 PV wire + #8 Gnd which go to solar panel 3 strings without conduit.

Now when I do my calculation for cable sizing Thwn-2 copper is 90 degree C only column ampacity table ampacity of 40A.

My more than 3 current carrying derating is 0.8

My roof temp correction factor is 0.76

My optimizer worst case Isc is 18A.

40x0.76x0.8 = 24

18x1.25 = 22

24>22.

My questions are following is in regarding 110.14(C) temprature rating:

1. Do my terminals, device have to be rated 90C?

2. If terminals or device are 75C then 40A would not be the ampacity and 75C would apply? If yes then Thwn-2 is not in 75C. What would be new amapcitty be?

3. Is their such a thing inverter rated 90C or inverter terminal rated 90C?

4. How does 110.14(C) apply to inverter terminals or inverter temp rating?


I appreciate your input. Not trolling but trying to clear things up please if possible forgive my ignorance.

Sent from my SM-G935U using Tapatalk
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have SE 14.4k inverter 208V three phase output. On the DC inverter side I have EMT conduit with 6 #10 Thwn-2 + #8 Gnd from inverter which is inside the building to outside to roof. On the roof under solar panels I have junction box which transtion cable to 6 #10 PV wire + #8 Gnd which go to solar panel 3 strings without conduit.

Now when I do my calculation for cable sizing Thwn-2 copper is 90 degree C only column ampacity table ampacity of 40A.

My more than 3 current carrying derating is 0.8

My roof temp correction factor is 0.76

My optimizer worst case Isc is 18A.

40x0.76x0.8 = 24 (ampacity after derating)

18x1.25 = 22 (what is needed)

24>22. So #10 awg THWN-2 is good given 40A at 90C insulation.

My questions are following is in regarding 110.14(C) temprature rating:

1. Do my terminals, device have to be rated 90C in above example for #10 THWN-2 to be good?

2. If terminals or device are 75C then 40A would not be the ampacity and 75C would apply? If yes then Thwn-2 is not in 75C. What would be new amapcity be?

3. Is their such a thing inverter rated 90C or inverter terminal rated 90C or are inverter DC rated for 90C?

4. How does 110.14(C) apply to inverter terminals or inverter temp rating?


I appreciate your input. Not trolling but trying to clear things up please if possible forgive my ignorance.

Sent from my SM-G935U using Tapatalk

No one knows or have any input?

Sent from my SM-G935U using Tapatalk
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
No one knows or have any input?

Sent from my SM-G935U using Tapatalk

Are you asking about DC or AC circuits? Are your inverter output circuits in rooftop conduit? What is the nameplate current rating of your inverter? What NEC code cycle is the AHJ on?

In general, you derate the 90 degree ampacity of your conductors for conditions of use (temperature and conduit fill) and the 75 degree ampacity for continuous use (X 0.8), and both results must be greater than Imax, which is 125% of Isc in "normal" DC strings, 15A with SolarEdge optimizers, or the nameplate AC rating of your inverter(s). The rooftop adder to the ambient temperature is mostly gone in the 2017 NEC.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Are you asking about DC or AC circuits? Are your inverter output circuits in rooftop conduit? What is the nameplate current rating of your inverter? What NEC code cycle is the AHJ on?

In general, you derate the 90 degree ampacity of your conductors for conditions of use (temperature and conduit fill) and the 75 degree ampacity for continuous use (X 0.8), and both results must be greater than Imax, which is 125% of Isc in "normal" DC strings, 15A with SolarEdge optimizers, or the nameplate AC rating of your inverter(s). The rooftop adder to the ambient temperature is mostly gone in the 2017 NEC.
I am asking in regards to 110.14(C) DC side. I am using THWN-2 #10 awg conductor up to juntion box on roof right at the solar panels. THWN-2 is found only in 90C column so amapcity #10 AWG is 40A Table 310.15(B)(16).

I am asking do the terminals, devices have to be rated 90C or can they be 75C or 60C for 40A ampacity of THWN-2?

However, I just maybe found the answer NEC 2014 Article 110.14(C) Temprature Limitations:

"...Conductors with temprature rating higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both...."

No?

Sent from my SM-G935U using Tapatalk
 

Carultch

Senior Member
Location
Massachusetts
I am asking in regards to 110.14(C) DC side. I am using THWN-2 #10 awg conductor up to juntion box on roof right at the solar panels. THWN-2 is found only in 90C column so amapcity #10 AWG is 40A Table 310.15(B)(16).

I am asking do the terminals, devices have to be rated 90C or can they be 75C or 60C for 40A ampacity of THWN-2?

However, I just maybe found the answer NEC 2014 Article 110.14(C) Temprature Limitations:

"...Conductors with temprature rating higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both...."

No?

Sent from my SM-G935U using Tapatalk

90C rated wire does not necessarily mean you need 90C terminals/equipment. It just means that 60C or 75C rated terminals become the "weak link" in the terminal-wire-terminal assembly. Most equipment in practice will be rated for 75C. This is the default for equipment over 100A, and while it is most common for equipment 100A and less, you do have a burden of proof in that case to use the 75C values. Because 100A and less, the default is 60C rated.

Generally speaking, 90C rated equipment is rare. Even if terminals are marked AL9CU, they have to be installed either in a separate enclosure from the equipment, or in equipment that is rated 90C as an assembled product.

The most common reason you get to take credit for the 90C rating, is for your derate calculations that go with bundling adjustments and ambient temperature corrections. These factors do not apply to terminations, they apply to the wire as a whole. So your ampacity is ultimately limited by the raw value of ampacity of the terminations, but you can take credit for the wire's 90C rating as your starting point for these calculations.
 
Last edited:

pv_n00b

Senior Member
Location
CA, USA
The terminal temperature rating usually relates to conductors terminated on an OCPD or an insulated terminal. Often if you land on a busbar with an uninsulated "9" rated lug you can use the full 90C rating of 90C conductor. For instance I've seen DC combiners where the fuse terminal are 75C rated and the output terminals that land on the busbar are 90C rated.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
90C rated wire does not necessarily mean you need 90C terminals/equipment. It just means that 60C or 75C rated terminals become the "weak link" in the terminal-wire-terminal assembly. Most equipment in practice will be rated for 75C. This is the default for equipment over 100A, and while it is most common for equipment 100A and less, you do have a burden of proof in that case to use the 75C values. Because 100A and less, the default is 60C rated.

Generally speaking, 90C rated equipment is rare. Even if terminals are marked AL9CU, they have to be installed either in a separate enclosure from the equipment, or in equipment that is rated 90C as an assembled product.

The most common reason you get to take credit for the 90C rating, is for your derate calculations that go with bundling adjustments and ambient temperature corrections. These factors do not apply to terminations, they apply to the wire as a whole. So your ampacity is ultimately limited by the raw value of ampacity of the terminations, but you can take credit for the wire's 90C rating as your starting point for these calculations.
Ok here is my question:
18A is Isc of the optimizer.
If i do 18x1.25x1.25= 28A then i need 28A.

Now without any temperature correction or any derating since my circuit is less than 100A I would take 60C but 60C does not have THWN-2 column so what would be the size if THWN-2 is provided?

Sent from my SM-G935U using Tapatalk
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
I am asking in regards to 110.14(C) DC side. I am using THWN-2 #10 awg conductor up to juntion box on roof right at the solar panels. THWN-2 is found only in 90C column so amapcity #10 AWG is 40A Table 310.15(B)(16).

I am asking do the terminals, devices have to be rated 90C or can they be 75C or 60C for 40A ampacity of THWN-2?

Virtually all terminations are rated at 75 degrees C. In most of Texas under the 2014 NEC, ambient plus rooftop adder (>3.5 inches off the roof) is 0.71. Conduit fill derate for 4-6 current carrying conductors is 0.8. #10 THHN-2 has a 40A ampacity @90 degrees and 75 degree #10 is rated at 35A @75 degrees. You must consider both the 90 degree number for conditions of use (heating of the insulation) and the 75 degree number for continuous use (heating of the terminals).

For 3 DC circuits (6 CCC's) in a single conduit >3.5 and <12 inches off the roof:

Conditions of use: (40A)(0.71)(0.8) = 22.7A
Continuous use: (35A)(0.8) = 28.0A

You must "beat" both those numbers. To account for excess insolation, your string Isc must be less than (0.8)(22.7A) = 18.16A
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Virtually all terminations are rated at 75 degrees C. In most of Texas under the 2014 NEC, ambient plus rooftop adder (>3.5 inches off the roof) is 0.71. Conduit fill derate for 4-6 current carrying conductors is 0.8. #10 THHN-2 has a 40A ampacity @90 degrees and 75 degree #10 is rated at 35A @75 degrees. You must consider both the 90 degree number for conditions of use (heating of the insulation) and the 75 degree number for continuous use (heating of the terminals).

For 3 DC circuits (6 CCC's) in a single conduit >3.5 and <12 inches off the roof:

Conditions of use: (40A)(0.71)(0.8) = 22.7A
Continuous use: (35A)(0.8) = 28.0A

You must "beat" both those numbers. To account for excess insolation, your string Isc must be less than (0.8)(22.7A) = 18.16A
Where do you see THWN-2 @ 75C in ampacity table?

Sent from my SM-G935U using Tapatalk
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
Where do you see THWN-2 @ 75C in ampacity table?

Sent from my SM-G935U using Tapatalk

You don't. You find it in the 90 degree column and look to the left. The temperature rating of a conductor is actually the rating of its insulation (copper is copper), but you don't want to overheat your 75 degree rated terminals, either.

The number in the 75 degree column tells you the maximum current in a conductor to keep the temperature below 75 degrees, but it has nothing to do with the rating of the insulation. A #10 copper wire with 35A in it gets it to 75 degrees irrespective of the rating of the insulation.

The COU derating of the conductor @ 90 degrees keeps the wire below 90 degrees to protect the insulation. The CU @ 75 degrees derating of the conductor keeps it below 75 degrees to protect the terminals. You run both calcs and the lesser of the two is your "real" ampacity.
 
Last edited:

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
You don't. You find it in the 90 degree column and look to the left. The temperature rating of a conductor is actually the rating of its insulation (copper is copper), but you don't want to overheat your 75 degree rated terminals, either.

The number in the 75 degree column tells you the maximum current in a conductor to keep the temperature below 75 degrees, but it has nothing to do with the rating of the insulation. A #10 copper wire with 35A in it gets it to 75 degrees irrespective of the rating of the insulation.

The COU derating of the conductor @ 90 degrees keeps the wire below 90 degrees to protect the insulation. The CU @ 75 degrees derating of the conductor keeps it below 75 degrees to protect the terminals. You run both calcs and the lesser of the two is your "real" ampacity.
I think i see what you are saying first determine how much current it would take #10 cable terminal to get to 75C which is 35x0.8=28A. Compare that to what you get after derating. If derated ampacity is less than terminal ampacity then ok. If greater then you take terminal ampacity.

Make sense where is all of this in NEC 2014? Which code section?

Sent from my SM-G935U using Tapatalk
 
Last edited:

Carultch

Senior Member
Location
Massachusetts
Ok here is my question:
18A is Isc of the optimizer.
If i do 18x1.25x1.25= 28A then i need 28A.

Now without any temperature correction or any derating since my circuit is less than 100A I would take 60C but 60C does not have THWN-2 column so what would be the size if THWN-2 is provided?

Sent from my SM-G935U using Tapatalk

The rule on 60C terminals is usually more academic than practical. It is a rule that applies in theory, for when equipment/terminals are not specifically listed for any temperature (which is rare). If you are taking an exam, you can't assume 75C by default like you can in practice. The exam problem would have to state it, or the exam would have to give it in a general statement for all problems. Most equipment you use, will be listed and labeled otherwise for 75C.

Don't expect to find a 90C rated wire in the 75C column. It is allowed to be sized for either a 60C or 75C rating, if other factors govern. THWN-2 being in the 90C column means that it is 90C rated and rated to everything lower than 90C. The breakdown of the term "THWN-2" means thermoplastic, heat and water resistant, with a nylon jacket and dual rating for 75/90C. One H = 75C, two H's = 90C, "-2" means dual rated for 90C in addition to the 75C rating it would have without it. THWN without "-2" is 75C rated in wet locations, and usually carries THHN rating allowing a 90C rating in dry locations. Most modern wire in this family is THWN-2 fully rated for both high heat and water, but check the datasheet if you depend on this being true. Some datasheets have fine print that don't carry the full rating in all sizes. You often will see THWN-2's print legend marked THHN/THWN/THWN-2, because it carries the legacy ratings of its predecessor products.

The rule about using both 125% factors, only applies to uncontrolled outputs of PV modules. It does not apply to inverters or DC/DC converters, which are current limited. The first 125% is for the possibility of more than a "full sun" illuminating the panel, such as reflection from the surroundings (glass building, snow, etc) making the irradiance more than 1000 W/m^2. The second 125% factor is the continuous load factor. It applies to continuous loads in general, to limit the risk of nuisance tripping the fuse or breaker. For inverter outputs and DC/DC converter outputs, the device is current limited. Your 18A value is used in place of 125%*Isc.

Back to your 18A optimizer output question. 18A*125% = 22.5A. #12 Cu wire carries a 25A rating at 75C. If it weren't for the "small conductor rule" in 240.4(D), #12 Cu would be our answer. If fusing is in place, you'd need #10 Cu to use either a 25A or 30A fuse, since #12 is limited to 20A fuses/breakers. What if fusing isn't in place? I hope some other members can assist on this one, because I rarely specify smaller than #10 on string wiring (other factors usually govern larger sizes), so I haven't researched how to rule out the need to apply 240.4(D).
 
Last edited: