K KWH Senior Member Jul 27, 2013 #1 I need to drop a outlet from the deck over a worktable in a commercial garage, is SJ or SO suitable for this with the proper supports.
I need to drop a outlet from the deck over a worktable in a commercial garage, is SJ or SO suitable for this with the proper supports.
V Volta Senior Member Location Columbus, Ohio Jul 27, 2013 #2 Either one. Table 400.4 lists both as suitable for pendants.
V Volta Senior Member Location Columbus, Ohio Jul 27, 2013 #3 Section 511.7(A)(2) allows these pendant cords to be installed above a Class 1 area, be aware of the boundaries / height.
Section 511.7(A)(2) allows these pendant cords to be installed above a Class 1 area, be aware of the boundaries / height.