K KWH Senior Member Dec 2, 2013 #1 I have 4 to 6 conductors in a conduit, when de-rating do you use the 90degree chart for thhn
david luchini Moderator Staff member Location Connecticut Occupation Engineer Dec 2, 2013 #2 KWH said: I have 4 to 6 conductors in a conduit, when de-rating do you use the 90degree chart for thhn Click to expand... Yes, you can use the 90 degree rating when applying an adjustment factor for number of conductors in a raceway. See 110.14(C).
KWH said: I have 4 to 6 conductors in a conduit, when de-rating do you use the 90degree chart for thhn Click to expand... Yes, you can use the 90 degree rating when applying an adjustment factor for number of conductors in a raceway. See 110.14(C).
kingpb Senior Member Location SE USA as far as you can go Occupation Engineer, Registered Dec 3, 2013 #3 Assuming those are current carrying conductors rated for continuous operation, I concur.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Dec 3, 2013 #4 kingpb said: Assuming those are current carrying conductors rated for continuous operation, I concur. Click to expand... Care to explain this?
kingpb said: Assuming those are current carrying conductors rated for continuous operation, I concur. Click to expand... Care to explain this?
kingpb Senior Member Location SE USA as far as you can go Occupation Engineer, Registered Dec 4, 2013 #5 infinity said: Care to explain this? Click to expand... 4 conductors - 3 phase circuit with ground; i.e. 4 conductors 6 conductors - 3 phase conductors, neutral, ground, and isolated ground; 6 conductors In both cases only 3 current carrying conductors.
infinity said: Care to explain this? Click to expand... 4 conductors - 3 phase circuit with ground; i.e. 4 conductors 6 conductors - 3 phase conductors, neutral, ground, and isolated ground; 6 conductors In both cases only 3 current carrying conductors.