I am looking to clarify a question on working spaces about electrical equipment over 600 volts.
<600 volts:
1910.303(g)(1)(i) states working space for equipment likely to require examination, adjustment, servicing or maintenance while energized shall comply with the following dimensions, except as required or permitted elsewhere in this subpart. Paragraph (A) refers you to Table S-1.
>600 volts:
1910.303(h) (5)(i) states Except as elsewhere required or permitted in this subpart, the minimum clear working space in the direction of access to live parts of electrical equipment may not be less than specified in table S-2.
Distances shall be measures from the live parts, if they are exposed, or from the enclosure front or opening, if they are enclosed.
Here is where my question is? Are the working distances still required if you can de-energize the > 600 volt equipment before testing and servicing? It would seem that there is no hazard if the voltages are enclosed or de-energized but the statement would seem to indicate the working distances are required either way.
<600 volts:
>600 volts: