Question on EMT support

Status
Not open for further replies.

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
When I was looking up info for another thread I found this on caddy's website. They were discussing 2020 updates.
I took a screen shot of it to share. Not to sure about the support where a coupling with in the ten foot support needing a additional support.
Unless it was showing a support where the structure supports are greater than ten feet from each other.

I hope there not saying if a coupling is with in This ten foot span and more than three feet from from the support that additional support is required.

Any way a pic.
 

Attachments

  • Screenshot_20231125-095140.png
    Screenshot_20231125-095140.png
    262.3 KB · Views: 44
Couplings have no bearing on the supporting requirements for EMT. I believe that back in the 90's the NEC had the word fitting included in the requirement but that has been removed.
 
Caddy probably just want to sell more parts. Or they were saying they have a product if the span is over 10' between supports.
I could be reading what they wrote incorrectly. Thanks for the reply
 
I think that you're right. The graphic exceeds the minimum code requirement but might get someone to buy more of their products.
 
Couplings have no bearing on the supporting requirements for EMT. I believe that back in the 90's the NEC had the word fitting included in the requirement but that has been removed.tje
Yes "fitting" was removed and replaced with "conduit body or other tubing termination" in the 1993 code. The substantiation said
SUBSTANTIATION: Reason: Provides consistency with other conduit support language and clarifies by removing the age old argument, "is a coupling a fitting?"
 