Table 430.22(E) makes no sense to me. Consider, for example, the conductors for an intermittent duty passenger elevator.
If the motor is a 5-minute rated motor, meaning it is designed to deliver its rated hp for periods of about 5 minutes, conductors may be sized at 85% of the motor nameplate current rating.
If the motor is a continuous rated motor, the conductors must be sized at 140% of the motor nameplate rating.
In either case, the motors are doing the same amount of work, for the same length of time, and assuming the motors are the same hp, drawing the same current.
It seems to me that it is the classification of service , and not the time rating of the motor, that determines how long the motor is going to run. Why,then, is the conductor size based on the motor time rating?
Thanks
Brian Dolan
Palos Park, IL
Thanks
Brian Dolan
Palos Park, IL