I am feeding to a step down transformer from a 480 volt panel to 240 panel, when figuring connected load on 480 panel do you use the connected load of the step down panel or figure a different way.
Thanks
You use the same VA (volt-ampere) load values, as some additional demand factoring may kick in on the 480V panel. There are those out there that simply carry the demand VA, but that is not the proper way IMO.I am feeding to a step down transformer from a 480 volt panel to 240 panel, when figuring connected load on 480 panel do you use the connected load of the step down panel or figure a different way.
Thanks
I am feeding to a step down transformer from a 480 volt panel to 240 panel, when figuring connected load on 480 panel do you use the connected load of the step down panel or figure a different way.
Thanks
The question posed is about calculating the load on the 480V panel. Sizing conductors is a completely separate consideration.Size them to carry the full VA of the transformer.
Where this is apparently supplying a general purpose lighting/appliance panelboard - good point, why not just run conductors/equipment that can carry full rating of the transformer.The connected load is the full VA rating of the transformer. Everything should be sized based on that.
Why would you install a transformer, then limit it's output by under sizing the panel, breakers, cable, etc?
The connected load is the full VA rating of the transformer. Everything should be sized based on that.
Why would you install a transformer, then limit it's output by under sizing the panel, breakers, cable, etc?
I'm not saying you can't figure it that way, but it is truly not the connected load. That would be connected plus future potential.... and that isn't even considering demand. Also there is no mention of load types. It is commonplace to upsize trannies for motor loads.Where this is apparently supplying a general purpose lighting/appliance panelboard - good point, why not just run conductors/equipment that can carry full rating of the transformer.
If it were supplying fixed equipment - there may be all sorts of reasons to provide the transformer they did.
30 kVA may not have been enough but 45 is next standard size? If it is a fixed load or there is slim chance of adding more load later, why run more conductor then it needs? Other conditions of the install may make difference in the decision here as well.
The connected load is the full VA rating of the transformer.
Why would you install a transformer, then limit it's output by under sizing the panel, breakers, cable, etc?
That is a design choice not a requirement.
Wouldn't it be the simple approach to use VA of transformer as the size, seems derating complicates the issue.