K KWH Senior Member Jun 22, 2015 #1 Do you figure 180va for each outlet in this snap together modular furniture or do you allow more, computers are the main device.
Do you figure 180va for each outlet in this snap together modular furniture or do you allow more, computers are the main device.
JoeStillman Senior Member Location West Chester, PA Occupation Electrical PE Jun 22, 2015 #2 I like to treat electrified furniture like a multi-outlet assembly. See 220.14(H). I use 180W for each 5' of electrified section.
I like to treat electrified furniture like a multi-outlet assembly. See 220.14(H). I use 180W for each 5' of electrified section.