We have a crew that disconnects and reconnects power for the Poco on residential properties due to non-payment. The Poco used to do this themselves but like allot of things they are using sub-contractors. One guy was sent to a church (3phase ) that has 2 separate drops from the transformer because electrician on site needed one drop cut loose, our guy cut the wrong drop then proceeded to cut the other drop and didn't identify any of the wires either time. I cant think of an excuse for this but talking to the guy on the phone it sounded like there was only 3 insulated conductors ( no reference to ground ) would a phase rotation meter be all you need to sort this out. The Poco was called and fixed the problem.and in his defense they only do single phase drops and should have never even been sent to this site, besides all the issues and mistakes that were made if you were called out on a existing sight 3phase drop cut loose nothing marked how would you troubleshoot this as a electrical contractor or the Poco.
Cutting a drop loose without marking can be a problem as some POCO's don't always follow a set CW or CCW rotation, a service with a grounded conductor can always be found by checking to something grounded like the metal riser pipe and is a test preformed by most line men when dealing with an unmarked service but this does not tell you what rotation was used before the drop was cut, even using a rotation meter will not tell you what the rotation was before the drop was cut, and about the only way to be sure is to pick one load that must have the correct rotation and only heat up that one load so it can be bumped and if it turns in the correct direction then all is good but if it doesn't then you need to swap two conductors, if dealing with a grounded B then you will need to swap A & B as the grounded B lands on C in the meter base if you have already crimped the drop then just swap at the main, also keep in mind that with CT metering the PT's have to correspond to the CT's so depending upon where the PT's and CTs are located and where the drop is cut this has to be maintained so sometimes it is just easier to re-cut the drop and swap the two conductors.
Some simple things to keep in mind:
Single phase:
The grounded circuit conductor can always be found by checking continuity to the riser pipe or meter base if metal so the other two are always the hots.
Or the grounded conductor can be the smaller of the three conductors but not always.
Three Phase
again the grounded phase or conductor can be found by checking to the riser pipe.
If the service is a Grounded delta (3-wire) the grounded B phase always lands on C in the meter base but lands on B at the main breaker.
Checking a motor load after finding the correct grounded conductor is the only way of being sure you have the correct rotation because if one is wrong they all will be wrong.
With a 4-wire delta finding the B phase is critical as landing 120 volt line to neutral loads on it can burn up allot of loads.
and depending upon where in the circuit the PT's and CT's are located, they must correspond to the correct phase so if phase A PT is on the phase that B ct is on the meter will not read correctly.
Most PT's are installed in the same place where the CT's are, like in the CT cabinet but watch out for pad mount as here the CT's and PT's are installed in the pad which should not be a problem as long as rotation and grounded conductor is found