Im reviewing some practice questions for my license exam, the question is the following.
2014 nec cycle
A 120v/208v wye service has a computed load of 350 amps. the neutral is considered a current carrying conductor as 52 percent of the load is nonlinear. it will be installed in RMC. what is the smallest THHN copper conductor that may be used.
choices are 400, 500, 600, 750 Kcmil
soo, the answer states that its 4 conductors. that i understand.
so we adjust by adjust by 80%
they show 600 as the correct answer
then it states if over 100 amps that we use 75deg column per 110.14 (C)1(b)1 and shows how 600mcm is used based on 90deg table to get 380amps after adjustment.
but doesnt 110.14 mean we have to use 75deg column? so 750mcm is actually correct??
would really like some clarification if possible thank you.:?:?