jango Senior Member Aug 24, 2011 #1 What are the rules or recommendations for having Knob & Tube wiring running visible throughout an attic and burying it all with blown in insulation? Any feedback on this would be greatly appreciated.
What are the rules or recommendations for having Knob & Tube wiring running visible throughout an attic and burying it all with blown in insulation? Any feedback on this would be greatly appreciated.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Aug 24, 2011 #2 Knob & tube should not have insulation blown ontop of it. Art.394.12 (5) specifically states this