I have a 200A meterbase disconnect with 8 spaces. It's going to feed a 150A existing panel. My plan was to get 2 pole 150A breaker and run 2/0 AL to feed existing 150A breaker. My issue is the 2 pole 150A breaker takes up 4 spaces and is so overly big it doesn't allow me to put any other breakers or surge protector on the opposite side of the Meter base disconnect.
Trying to come up with what to do. Do I buy a different surge protector and mount it in the 150A existing panel and continuing using the 2 pole 150A breaker in meter base making the meter base completely full?
Is there anyway an inspector would pass using 2/0 AL on the feed through lugs in the 200A meterbase if it is protected downstream by a 150A main breaker panel?
Or am I better off ordering new 4/0 AL wire and going directly on the feed through lugs to his existing 150A panel? Will the inspector ask for load calcs if I go with 4/0 4/0 and 2/0 for neutral?
Thanks for all the help
Trying to come up with what to do. Do I buy a different surge protector and mount it in the 150A existing panel and continuing using the 2 pole 150A breaker in meter base making the meter base completely full?
Is there anyway an inspector would pass using 2/0 AL on the feed through lugs in the 200A meterbase if it is protected downstream by a 150A main breaker panel?
Or am I better off ordering new 4/0 AL wire and going directly on the feed through lugs to his existing 150A panel? Will the inspector ask for load calcs if I go with 4/0 4/0 and 2/0 for neutral?
Thanks for all the help