Dogtrooper
Member
- Location
- Troy, NY, USA
Hello. I have a question regarding the total of amp form adding up all branch circuit breakers in a panel compared to the main circuit breaker. I have ask tons of fellow electricians and several engineers and electrical inspectors. No one can pin point a code section(s) or something in writing that explains why.
Here is a senerio.
You have a 200amp service 120/240 volt service.
Main breaker is 200 amp.
There are 2 150amp 2 pole branch circuit breakers in the panel.
I'm being told by a power company that this is illegal.
Myself and every other electrical professional I know or talk to says that this is legal.
If you look in any panel in just about any building the branch circuit breakers ratings most always add to more than the main breaker rating.
I know this is figured using load calculations And as long as the total load is under the rating of the main breaker ( using proper calculations and percentages from the nec of course) that it is ok.
I'm looking for something that explains this to the average person that does not know about electric.
The owner is questioning me about why and other than because this is how it is done. I cant explain it to him.
So I have a power company guy telling me this is wrong. And the owner now not trusting me that it was done right.
Is there any help you could give in helping me explain this to the power company and the owner of the building that this legal.
Thank
Here is a senerio.
You have a 200amp service 120/240 volt service.
Main breaker is 200 amp.
There are 2 150amp 2 pole branch circuit breakers in the panel.
I'm being told by a power company that this is illegal.
Myself and every other electrical professional I know or talk to says that this is legal.
If you look in any panel in just about any building the branch circuit breakers ratings most always add to more than the main breaker rating.
I know this is figured using load calculations And as long as the total load is under the rating of the main breaker ( using proper calculations and percentages from the nec of course) that it is ok.
I'm looking for something that explains this to the average person that does not know about electric.
The owner is questioning me about why and other than because this is how it is done. I cant explain it to him.
So I have a power company guy telling me this is wrong. And the owner now not trusting me that it was done right.
Is there any help you could give in helping me explain this to the power company and the owner of the building that this legal.
Thank