Ok here is the scenario:
I have a 900ft between an EDR (electrical distribution room) and a Communications Room. I will be runnning a feed from the DB(distribution board) in the EDR to a DP(distribution panel) in the Comm. Room. I use 208/120VAC in both rooms. For voltage drop purposes, I will be stepping the voltage up before the 900ft conduit run to 480V then stepping it back down to 208/120VAC. Can someone tell me the pros and cons to the following setups:
1) At the EDR end, using a delta primary - delta secondary step up transformer (112.5kVA), then only running 3 cables (500kcmil) in the conduit. Then using a delta primary - wye secondary step down transformer (112.5kVA) at the Comm. Room end.
2) At the EDR end, using a delta primary - wye secondary step up transformer (112.5kVA), then only running 3 cables (500kcmil) in the conduit but grounding the neutral. Then using a delta primary - wye secondary step down transformer (1125.5kVA) at the Comm. Room end.
I would like to add that there will be no loads tapping the 900ft run where the voltage is 480/277VAC. The 480VAC is only for tranmission purposes so allow less conductors to be ran using 208/120VAC.
thanks
If there is any unclarities, please let me know
[ March 21, 2005, 12:46 PM: Message edited by: stcalle ]
I have a 900ft between an EDR (electrical distribution room) and a Communications Room. I will be runnning a feed from the DB(distribution board) in the EDR to a DP(distribution panel) in the Comm. Room. I use 208/120VAC in both rooms. For voltage drop purposes, I will be stepping the voltage up before the 900ft conduit run to 480V then stepping it back down to 208/120VAC. Can someone tell me the pros and cons to the following setups:
1) At the EDR end, using a delta primary - delta secondary step up transformer (112.5kVA), then only running 3 cables (500kcmil) in the conduit. Then using a delta primary - wye secondary step down transformer (112.5kVA) at the Comm. Room end.
2) At the EDR end, using a delta primary - wye secondary step up transformer (112.5kVA), then only running 3 cables (500kcmil) in the conduit but grounding the neutral. Then using a delta primary - wye secondary step down transformer (1125.5kVA) at the Comm. Room end.
I would like to add that there will be no loads tapping the 900ft run where the voltage is 480/277VAC. The 480VAC is only for tranmission purposes so allow less conductors to be ran using 208/120VAC.
thanks
If there is any unclarities, please let me know
[ March 21, 2005, 12:46 PM: Message edited by: stcalle ]