Kyle_Edwards Member Location Muskogee Occupation EE Jun 30, 2021 #1 Working on panel dealing with UL mark labels on it The UL mark on wire insulation is adequate traceability?
Working on panel dealing with UL mark labels on it The UL mark on wire insulation is adequate traceability?
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Jun 30, 2021 #2 Kyle_Edwards said: Working on panel dealing with UL mark labels on it The UL mark on wire insulation is adequate traceability? Click to expand... Traceability is not something required of UL508a panels. The requirements for conductors are found in the standard in paragraph 29.2. Most people use MTW wire because it is easy to work with and quite robust.
Kyle_Edwards said: Working on panel dealing with UL mark labels on it The UL mark on wire insulation is adequate traceability? Click to expand... Traceability is not something required of UL508a panels. The requirements for conductors are found in the standard in paragraph 29.2. Most people use MTW wire because it is easy to work with and quite robust.