Ok in the NEC 2002, Article 430.6(A)(1) through 430.6(A)(2) says to use the FLA(full load amps) from the tables to size motor circuit components, then use motor nameplate current to size the overload protection.
Just sticking to what the book says this is how I would go about sizing the motor components. Someone at my job said that you would do this in the event that you do not have the nameplate information for the motor.
There point is that if you have the values from the motor nameplate, then you would use those primarily to what the code is saying to do. Meaning when you size your conductors, branch circuit protection, etc. you would use the current rating from the nameplate.
This seems to contradict what the code is saying because it explicitly says that use the FLA from the motor tables to size cetain components and use the nameplate current rating to size the overload protection.
Can anyone clear up this unclarity?
thanks
Just sticking to what the book says this is how I would go about sizing the motor components. Someone at my job said that you would do this in the event that you do not have the nameplate information for the motor.
There point is that if you have the values from the motor nameplate, then you would use those primarily to what the code is saying to do. Meaning when you size your conductors, branch circuit protection, etc. you would use the current rating from the nameplate.
This seems to contradict what the code is saying because it explicitly says that use the FLA from the motor tables to size cetain components and use the nameplate current rating to size the overload protection.
Can anyone clear up this unclarity?